Variable Frequency Drives (aka "VFD;s" or just "Drives")
These are electronic control boxes that let you run AC motors at variable speeds, not just the nameplate RPM.
They also allow varied acceleration rates, which can reduce start up currents & allow a big motor to run on a small power source. Almost all of them are only compatible with 3 phase motors. Most use 3 phase power as a primary power source. Some can use single phase primary power. A few have been set up to use DC primary power. Most can run motors at lower voltage than the primary power. A few can run motors at higher voltage than the input power. Most will let you run variable torque as well as variable speed, but that is not of particular interest when running a compressor. Some can communicate over a wide variety of comm buses like device net, Profibus, Canbus, Ethernet, Fiberoptix, etc., but the ones I will discuss here are some of the most basic that only need a couple of buttons & maybe a turn dial to control them.
There is a wide variety of drives out there these days that let you also control other aspects of motor response, but those are beyond the scope of running something as simple as a compressor.
When selecting a drive, you need to start with a few basic questions -
Is my motor the proper type for the drive (usually you need a 3 phase motor)
Is my motor the correct voltage for the drive?
Is the drive's capacity big enough to handle my motor? The rating can be in HP or Kw (1hp = 0.746kW)
Is the drive controlled by push buttons & maybe a dial that are on the unit itself, or does it need external controls?
Do I have space to mount the drive somewhere? Preferably mount it where it will not get shaken to death.
Do I have a power source that can run the drive. Some 3 phase output drives can run on single phase input, but the amps in will be much greater than the amps out in this case.
Is my compressor in a wet location? If so, is my drive rated for this? Or do I need an enclosure? Will an enclosure derate it's power capacity?
A few advantages to consider would include -
Drives can be useful when you want to run a 3 phase motor from a single phase power source. This is of interest to anyone with a 3 phase compressor that wants to us it in a home that only has single phase power available.
Drives can start up the motor slowly, which reduces starting current & will likely allow you to run a 13 amp motor on a 15 amp circuit that would have tripped out from a normal motor start up. Locked rotor current at motor start up is typically calculated at 6 times nameplate current. Most supply circuits can take a certain amount of inrush for a short time, but motor start loads can be pretty big and often trip out circuits that are close to nameplate current.
The variable speed feature may be useful in nitrox blending operations, for fine tuning the mix, provided that the compressor is OK to run at the different speeds. I don't currently have information on what range of speeds compressors can run at. I have noticed that a factory original Bauer Jr with an electric motor is set to run a couple of hundred RPM slower than one that runs off of a gas or diesel motor, so there does seem to be at least some range in acceptable speed.
The external control features on most drives make it easy to tie in something like an automatic shut off switch that is controlled by pressure or temperature. Most can be set to monitor things like the current they are consuming, line voltage, heat sink temperature, etc. & many can be set to activate an alarm or shut down the unit when a selected parameter reaches a preset value.
A slow start up may reduce battering of floating pistons, & may reduce other mechanical wear in the compressor.
When running below the nameplate RPM of the motor, the drive is in the constant torque mode & full motor torque is available. When running above nameplate RPM, the drive is in constant horsepower mode, & the torque reduces as speed increases. When running below nameplate RPM, you are running at reduced Horsepower. Because of this, it may be possible to run a 5 hp compressor on a power feed that is only suitable for 3hp, if you run the 5hp motor at sufficiently reduced speed, & therefore sufficiently reduced effective hp.