- Messages
- 20,647
- Reaction score
- 15,141
- # of dives
- I'm a Fish!
I'm going to say it shouldn't. Without seeing the specifics of your wiring diagrams I can't confirm that for sure. You will have to look at the box and preferably a diagram if it is available to see. There were so many variants of these that it is almost impossible to say for sure. In an ideal world the control system is only tapping onto 1 or 2 of the phases and wants either 120vac or 240vac input *208 on 3p, but 200ish volts, for controls they aren't too picky*. If that's the case then the VFD goes after the main power switch and the only thing on the output is the motor. If for whatever reason they used all 3 phases for the controls then you have to put it where the 3p plug was. Most of the controls don't care about frequency and you're only using it for soft start and stop so they'll get 60hz all the time anyway, but it is technically best practice to only have a motor on the output side of the VFD and all controls before hand.Thank you for the information. I actually spoke to wolf automation and ordered a VFD from them. Everyone convinced me it was the best way to go. The only question I have is about controls. Will the VFD effect my controls at all?
If you have the wiring diagram then please post it, if not, please take some good pictures of the inside of the electrical box and we can try to back through it