One safety is to set the setpoint to 40 and dial back the o2 regulator to a max of 1-2 PSI above what you are really wanting (eg. 34% for a 32% mix). Then change your setpoint to what you really want. This will provide an upper bound if the proportional control valve gets stuck open. One nice thing about a PID control is that it works off of the error reported between the setpoint and reading. So if the compressor cuts off, and the o2 in the mixer goes up, and up as if it is trying to go to 100%, the proportional valve will keep trying to reduce the o2. Quickly closing the valve and cutting off the o2. I tested this last night. I had the mixer set to 32%. This is an 8 cuft/min compressor. When the compressor shut off, the spike in o2 across the mixer chamber in the nitrox stick only spiked to 35% before the valve closed entirely. A lower-volume compressor would most likely experience less of a spike.