Neutral to or through the case does not sound good (or code compliant) at all.
Welcome to ScubaBoard, the world's largest scuba diving community. Registration is not required to read the forums, but we encourage you to join. Joining has its benefits and enables you to participate in the discussions.
Benefits of registering include
If all you have coming in to the case for 240V is two leads then both of them are hot. There is a missing neutral. I would recommend hiring an electrician to do this job. It already sounds like it isn't up to code. You don't need a transformer to step 240V down to 120V, you can tie into one leg and the neutral and you'll have a two wire 120V circuit.
this is for a fan to sit on top of the comprerssor to give extras cooling from a 21 inch house fan. I wanted to pt a timer onthe outlet to let the fan run for a while after the compressor shuts down.I’d run two identical fans is series
I reread the initial post and using the case for a neutral is NOT allowed. Yes they used to do this with electric clothes dryers but no more, for the simple reason being it could float to potential if the ground is compromised or disconnected. What Mr Wookie is saying about high leg is usually in a commercial building. I have dealt with it when someone decides to put a restaurant in a sorta residential area and the power company is on the cheap and fast answer mode. If a high leg is there it MUST be marked as such.
From what I have read,,,the simple option, assuming, and we all know what that means,,,he has just 240 v coming into the controller, would be purchase a 240 volt fan. Yes they are made and would stop the addition of a transformer, rewiring, and additional controls. The fan would add a small amount of current on the load side and not affect the compressor operation. Assuming, yes here we go again, it is not a large commercial fan. Keep it simple and you should not need an outside electrician to overcharge and do a major renovation on the controls or feeder.
From the panel to the street neutral and ground are tied togetherTo find a 240 fan would be the simplest. Right now I have a2 hots and a grounding lead coming from the panel. the grounding and neutral are electerically the same in my panel . I donot have a neutral bus and a grounding bus. they use the same strip as they are tied together.
Per NEC, ground only bonds to neutral at the service entrance. Bare wires & green wires are on the ground buss. White wires are on the neutral buss. Yes the two busses are connected by a bonding bar, but you should not have white wires on the same buss as a green or bare wire. If you do, then your box is probably not wired to modern code. No you are not allowed to connect a neutral load wire to a green or bare wire that goes to a ground buss (even though it will usually make the device function).To find a 240 fan would be the simplest. Right now I have a2 hots and a grounding lead coming from the panel. the grounding and neutral are electerically the same in my panel . I donot have a neutral bus and a grounding bus. they use the same strip as they are tied together.