no I meant using a 5-10 horse motor driving a 3 ph generator to make the 3ph for the motor. I doubt that he has 3 ph at his location only 220 1ph from the power line. with larger than 5 hp motor it would not draw the high end per design power from the house. Run the larger motor at half load capability rather than a 5 hp running at say 90% load capacity
use a 2x rated VFD to do the phase conversion. Way more efficient, and much cheaper. I.e. a 10hp VFD to run a 5hp motor. Technically it's sqrt(3), but with the increments that motors and drives are typically sized, 2x is as close as you'll get with small motors. 40hp is I think the first size where you get get away with not sizing 2x by using a 75hp drive instead of an 80hp, but that's also a 200a circuit and is WAY outside of any discussion we have going on here...