All compressed gas cylinders used in North America are governed by The US Code of Federal Regulations Title 49. The US Department of Transportation is specifically charged with enforcing Title 49 as well as other sections of the CFR. These aren't optional - they are the law. If a company is found to be out of compliance with these regulations they can be cited and fined by the DOT, OSHA or both. Flagrant violation can be subject to prosecution. In other words, complying with them is not optional.
Section 173.301(a)(1) of Title 49 states:
Except as provided in paragraphs (f)(5) and (f)(6) of this section, a cylinder filled with a gas and offered for transportation must be equipped with one or more pressure relief devices sized and selected as to type, location, and quantity, and tested in accordance with CGA S-1.1 (compliance with paragraph 9.1.1.1 of CGA S-1.1 is not required) and S-7. The pressure relief device must be capable of preventing rupture of the normally filled cylinder when subjected to a fire test conducted in accordance with CGA C-14 (IBR, see § 171.7 of this subchapter), or, in the case of an acetylene cylinder, CGA C-12 (IBR, see § 171.7 of this subchapter).
As you can see from the above, Title 49 refers to CGA S-1.1 as the governing document. Safety assemblies used in North America must be "in accordance with CGA S-1.1". CGA S-1.1 is too big to summarize in a few sentences. But among other things incorporated into CGA S-1.1 is that only manufacturer's original equipment safety assemblies may be used in any particular valve. The most abused aspect of this in the scuba industry is the practice of "double disking" and if one can find an original manufacturer's original equipment that is intentionally double disked, then they may be used with the manufacturer's permission. Since no responsible manufacturer would ever support that practice, it cannot be done legally. If one decides to "improve" a safety assembly by double disking it, then they are not in compliance with Federal law - in addition to being responsible for creating an extremely dangerous situation. If a safety assembly is double disked, the cylinder then becomes the weaker link.
The question of why North America uses safety assemblies and Europe does not is a much longer discussion. It started out as a philosophical difference of the risk/benefit of a safety assembly. But once that decision was made by the governing bodies (and that was a very long time ago), cylinders were then designed based on the knowledge that safety assemblies would either be used or not used. Believe it or not, the primary purpose of a safety assembly is to prevent a cylinder from rupturing in a fire situation - not as an overfill prevention device.
Double Disking a valve is almost obsolete today since the major valve companys have moved to a one piece saftey assembly. Thermo, Sherwood, soon SanoSub, Genesis all use a single piece assembly to prevent double disking.
A properly serviced valve with the saftey replaced with at least each hydro test date ensures that the valve remains in spefication for the cylinder it is used. When we service cylinders in our operation we inspect and replace safteys as routine, if it has been doubled up ... it is no longer.