Not much different 380, 400 3ph, should draw around 8 amps. Dial is hard to read look close make sure it’s set to the FLA written on the motor name plate.
Welcome to ScubaBoard, the world's largest scuba diving community. Registration is not required to read the forums, but we encourage you to join. Joining has its benefits and enables you to participate in the discussions.
Benefits of registering include
Closer to 12Not much different 380, 400 3ph, should draw around 8 amps. Dial is hard to read look close make sure it’s set to the FLA written on the motor name plate.
Only with a very low PF.Closer to 12
At full load it shouldn't have a low power factor. I was fudging low to make sure I wasn't wrong. I wasn't. 5.5 KW has to be about 7.5 hp.Only with a very low PF.
Typical 460v 3 phase motor amps are 1.3 times HP. This varies of course. 5.5 KW is about 7.5 hp. 5500 watts divided by 746 watts per HP comes close to 7.5 HP. The amperage number drops with higher voltage and rises with lower voltage, even on the same winding setup. Running a 460 volt motor at 490 uses less amperage, at 440, more.Awww I didn’t assume HP, just went with 5.5KW at 400 volts. Also the wire gauge looks small for a 7.5 HP motor to me anyway.
I(A) = 1000 × P(kW) / (√3 × PF × VL-L(V) )