That might be looking at things a bit too simplistically. The way things get certified by BAM or others is mostly as a unit, not as a single component. That’s because how the parts are used is often much more important than what material they’re made of.

Oxygen fires are never the result of a single failure, but a chain of things going wrong. Start with slight contamination on a polymer surface, couple that with adiabatic heating from rapid pressurisation, and add a thin or porous piece of polymer nearby and you’ve got the beginning of an incident. If that happens to be close to a thin metal spring, it might be the next in line to catch fire, and so on it goes.

Zytel is a proprietary blend of a polyamide, meaning it belongs to the same class as nylon, as rjack pointed out. Nylons do not exhibit great properties for oxygen service. Nylon 6/6, for example, has a comparatively low auto-ignition temperature (~240°C in 103bar oxygen), relatively high heat of combustion (~32,000J/g), and a poor oxygen index (~26%).
Zytel comes in many different varieties. Most often you’ll find Zytel 42 or Zytel 101 used as seat materials. Most Zytel blends fall into the same ballpark as other nylon or polyamide blends. Zytel 42, for example, has an auto-ignition temperature of ~180°C in 103bar oxygen, produces ~34,000J/g of heat, and has an oxygen index of around 34%. By any measure, these numbers are poor.

Yet many manufacturers specifically use Zytel blends in their oxygen-compatible product lines. Sherwood uses Zytel 101 in their medical post valves (KVAB and KVAC series). Poseidon uses Zytel as a seat, though I don’t know which blend, in their oxygen-capable regulators. Aqualung uses Zytel in the gaskets of the burst disc assemblies on their combat swimmer bailout cylinders. Cavagna uses a polyamide as the seat material in their oxygen valves. And the list goes on.
So why are polyamides with such poor oxygen compatibility characteristics so often used in oxygen service? The answer lies in how and where the parts are placed within the assembly. Leaving aside their oxygen characteristics, Zytel has excellent mechanical properties and is relatively stable in static oxygen environments.

Take the Sherwood KVAB medical post valve, for example:
View attachment 899107
If you follow the trail of gas through the valve, it becomes clear that the Zytel seat surface isn’t where adiabatic heating would occur. Nor is it directly in the gas path when the cylinder is being filled, meaning particle impacts are of no significance. Particle impacts could be an issue when the cylinder is emptied, as the seat surface is then directly in the gas path. However, thanks to the Joule–Thomson effect, the gas cools down during expansion, which significantly reduces the risk. The whole valve is incredibly well-engineered, keeping the polyamide seat away from danger zones. Where adiabatic heating could occur, under the packing nut, you’ll find PTFE, Viton, and copper as sealing materials. Even the spring is cleverly hidden for the most part within the seat.
A similar logic applies to the Poseidon seat when it’s inside an Xstream. The alloy ball takes most of the “heat,” so to speak. It isn't the Zytel that would take is exposed to the worst.

Now contrast that with this Z-Valve:
View attachment 899108
The valve’s seat is directly exposed to the gas flow when the cylinder is filled. Particle impacts and adiabatic heating can both hit the seat surface head-on. No matter what super-material you use, the engineering of this valve almost rules it out from ever being oxygen-compatible.

I always find it very helpful to mentally map the gas flow and follow it step by step to identify critical areas in terms of oxygen safety.

I write all this because I found the notion that the part is certified for 300 bar of oxygen too simplistic. I can almost guarantee that the part would ignite easily if exposed to rapid adiabatic heating and a bit of contamination. The point is: the way it’s placed in a Poseidon regulator, or the way the Zytel is used in a Sherwood KVAB valve, almost completely removes the part from the genuinely dangerous areas of the assembly. The whole Poseidon, as an assembly, is resistant to 300 bar of oxygen, but that doesn't mean that all its individual components, when removed from it, will be resistant as well.
The most resistant seat materials for oxygen service are mostly halogenated, but they are seldom used in breathing scenarios, or outright banned in some countries (France) due to the risk of carbonyl fluoride or phosgene developing even under partial combustion. Polyamides and other hydrocarbons, on the other hand, develop "only" carbon monoxide as a toxic gas, but carbonyl fluoride is at least ten times more deadly, while phosgene is probably even worse, being one of the gases used in World War I.

I have no idea what your adapter looks like, so I can't give you specific recommendations on whether the part is suitable or not. I'm not saying that it isn't, or that it's not a good idea, but it might be worth to stop for a minute and think about. I would suggest that if you substituted the part, you mentally map the gas flow and ensure it isn't exposed to any dangerous zones. In the end, every single polymer today will ignite happily if the conditions are just right and it is up to the engineer to develop the assembly clever enough that it is removed from danger zones.

I apologize for the long post, but felt the distinction was worth pointing out.

Back to your original question: I know of no threadlocker that is certified for 100% oxygen at high pressure. I’d actually be very surprised if such a product existed, as the market would be tiny at best. I’d prefer a mechanical locking method. If you can fit a washer, then split washers, Belleville washers, wave washers, or Nord-Lock washers could be great alternatives. If that’s not feasible, gentle staking can work well to lock the screw in place, as happy suggested. It doesn’t take much staking to stop a screw from turning. Ever so slightly and gently bending the screw can be feasible as well.

PTFE tape wouldn’t be my first choice either, as there's still a risk the screw could come undone. If that happens, you might end up with thin strands of PTFE tape floating in the oxygen path, and those are perfect fuel for combustion.
Thank you for the great explation. 8 of those BPVs have been in use for 10 years now, no explosion. Either my construction is perfect or I had a lot of luck. I guess it was luck :)
Anyway I will keep this construction as it is. Apart from adding a thread lock, but which one?

Thanks for all the advises, please go ahead.
 
Blind as a bat LOL

Here you go enclosed below the BAM certificate for oxygen (but you won't like it)



It's not difficult It's impossible besides pretty much all the so called BAM approved suppliers are supplying all pretty much the same type of "super" glue for a 1 to 40 bar range and LOX application and its only folk like hospitals with gaseous 6 to 8 bar lines and Liquid LOX that even require this particular type of BAM certification.

So your back again to £10 and Loctite 290 in a small 5Ml bottle. As I stated earlier

Incidentally the difference in strength is a consideration and is normally around the colours from Blue green to Red on increasing strength (I did say small blind threads) and care taken not to snap the thread on removal if too strong a glue used. As with the more thixotropic "Super Glues" for the 10mm bolts and above you use then on a small thread and snap it.

For example on a typical multi stage 200 bar pure oxygen compressor. As typical a couple of 6/32" or 5mm threaded screws would be used to hold an interstage reed valve to the valve plate.

This would call for a spot of Loctite 290. The application would be a spot of glue on the thread only
lower end. Then wiped off with a paper towel to remove most of the glue leaving only the thread and not up onto the undercut around the screw head or on the screw crest making sure its only on the screw thread root.

If the glue can be seen after fixing or leaks out or gets under the reed itself then it's removed entirely and the process starts all over again. Working pressure 40 bar. All parts in a higher pressure require a completely different design and screws or loctite glues would not be used.

In your application the glue is dry hardened and the hole is blind.
The thread is not over 6mm and you removed all the excess glue before fixing
The temperature is low ambient to 60C and the gas is not dynamic as in a compressor
or adiabatic loaded or affected by an pulsations .
The application gas stream has no particulate contamination and the gas velocity is conservative.
The amount of glue is too small to cause a kindling effect in the extreamly unlikely event of combustion.
https://datasheets.tdx.henkel.com/LOCTITE-290-en_GL.pdf page 3, Loctite 290, this product is NOT recommended on pure oxygen. Not even at ambient pressure. Reading this I wonder if Therabond would be a better (or less bad) product? Price does not matter as long as we are not talking about hundreds of $s.

Reading this I wonder if
 
https://datasheets.tdx.henkel.com/LOCTITE-290-en_GL.pdf page 3, Loctite 290, this product is NOT recommended on pure oxygen. Not even at ambient pressure. Reading this I wonder if Therabond would be a better (or less bad) product? Price does not matter as long as we are not talking about hundreds of $s.

Reading this I wonder if
Sorry Permabond, not Therabond
 
https://datasheets.tdx.henkel.com/LOCTITE-290-en_GL.pdf page 3, Loctite 290, this product is NOT recommended on pure oxygen. Not even at ambient pressure. Reading this I wonder if Therabond would be a better (or less bad) product? Price does not matter as long as we are not talking about hundreds of $s.

Reading this I wonder if

It really does't make any difference as it's basically the self same stuff. They all are whoever brand you call it and get to print the label on the bottle.
One gets tested under BAM an independent test house that would test a wooden tent peg for oxygen if you pay them and get a result. The other for legal and liability reasons choose not to bother with the European BAM test house and find it easier for (American) liability reasons to cover themselves with a disclaimer.

Now apart from the thixotropic difference between High Strength Medium and Low Strength and the difference in the colour dye used we are talking about the same stuff.

Now a small 3/32 or 5mm blind thread and with a capped nut or domed screw ensures the oxygen never actually sees the hardened glue material. Further the small amount of glue component is less than a drop and at that most is cleaned away with on the smallest amount of compound on the thread root only.
 
It really does't make any difference as it's basically the self same stuff. They all are whoever brand you call it and get to print the label on the bottle.
One gets tested under BAM an independent test house that would test a wooden tent peg for oxygen if you pay them and get a result. The other for legal and liability reasons choose not to bother with the European BAM test house and find it easier for (American) liability reasons to cover themselves with a disclaimer.

Now apart from the thixotropic difference between High Strength Medium and Low Strength and the difference in the colour dye used we are talking about the same stuff.

Now a small 3/32 or 5mm blind thread and with a capped nut or domed screw ensures the oxygen never actually sees the hardened glue material. Further the small amount of glue component is less than a drop and at that most is cleaned away with on the smallest amount of compound on the thread root only.
Looking at the drawing I think glues does see oxygen. It is not in the full gas stream, so far so good.

So you think I can simply use any Loctite low strength? Such a product is laying around here.
 
Do you think I can use any kind of Loctite?
 
OMG I see the drawing was not attached, sorry. Here it is. Right yellow screw must be locked a littel bit, thread is M13x0.5.

Brown part is made of SS, giving support to Zytel seat.
Right yellow screw holds Zytel on place. I must not screw it in with lot of torque, otherwise it will squeeze Zytel. Therefor screw can easily get loose, which happened 2 times.





View attachment 899114
If I am reading that right...
Yellow on the right has external threads that screw into the body? Looks like a spring retainer that is hollow and a pass through. Are there exposed threads in the body? If the yellow part screws in far enough to expose threads in the body, could you make a lock nut (I guess hollow bolt since external threads instead of internal?) to the right of the yellow part that screws into the body to hold it in place. A set screw, but hollow.

Another option. that countersink on the right of the spring. To the right of the lip the spring is against. Anything go in there? Could that be slit and tapped? A tapered (hollowed) plug screwed in. Expand the tail of the yellow part to lock it into the body? A drilled out pipe plug to put it simple.

I tried zooming in on the drawing, but lost resolution and can't read the details. Looking for mechanical solutions before putting chemicals in. Even if compatible with Oxygen, any concerns about off-gassing? All of the thread lockers I can think of are anaerobic (cure in the absence of oxygen). Putting them in an oxygen environment might make for a curing issue.
 
Yes you are reading that right. Unfortunately there is no exposed thread in the body and I need any free millimeter on the right side because the DIN connector comes in there.

Very good ideas but here they do not work.

Hm, never thought about off-gassing, very good point.

Your thoughts about mechanical solutions brought me to an other idea. I will try this out and report here.

Thanks so far to everybody for your help.
 
Here I attach the drawing once again, perhaps resulution is better. On my big screen I can read any detail even if quality is not the best. So Broncho perhaps it's a question of screen.
 

Attachments

  • RSV Var. 1 Stand 2022-08.JPG
    RSV Var. 1 Stand 2022-08.JPG
    116 KB · Views: 17
I found the solution to my problem. I added an O-Ring on the left part of the right yellow screw. See blue ring on drawing. Here we have 9.6mm outside diameter and 12.5mm inside diameter, I use a 9.25x1.78 mm o-ring. It gets squeezed a little bit, this works as a screw lock.

No Loctite needed, no off gasing, no problem.

Thanks to everybody helping me, you brought me to the o-ring-solution. Great forum here.